Just to add another picture, here's one on the left of this photo I took at Pluckley last month. I wondered what it was at the time!

15366587411_e9a4424d1c.jpg
 

Elecman

Established Member
Joined
31 Dec 2013
Messages
2,903
Location
Lancashire
It can be very difficult to get a good earth connection of a low enough impedance value to guarantee that any fault voltage at the cabinet can be lower than 50 volts which is the accepted safe value
 

dysonsphere

Member
Joined
22 Jan 2013
Messages
518
It can be very difficult to get a good earth connection of a low enough impedance value to guarantee that any fault voltage at the cabinet can be lower than 50 volts which is the accepted safe value

Indeed especially on made up ground like platforms but cant see it being a problem in open country side, or could it also be the parts of the cabinet arnt bonded internally, ie the doors etc.
 

edwin_m

Veteran Member
Joined
21 Apr 2013
Messages
24,925
Location
Nottingham
That's what more modern installations have. Older ones don't, hence the tent.

Considering that it is probably easier to earth a cabinet than to put a tent over it, there must be some reason why they didn't do that. I assume the cabinets were designed to be "floating" (electrically speaking) because of the risk that "earth faults" can lead to wrong side failures.

Have any of these tents been noted on 25kV lines? On these routes everything should be earthed anyway.
 

brianthegiant

Member
Joined
12 May 2010
Messages
588
Indeed especially on made up ground like platforms but cant see it being a problem in open country side, or could it also be the parts of the cabinet arnt bonded internally, ie the doors etc.

Getting a low earth impedance can be very challenging depending on the ground conditions. Slate has very high resistance. My guess is that railway embankments on clean ballast also have high resistance as they're relatively dry.

The ground resistance is less of a problem if you have a network of electrodes so the total area of your electrode field is large, for a single electrode it is more challenging.
 

Elecman

Established Member
Joined
31 Dec 2013
Messages
2,903
Location
Lancashire
Indeed so the requirement is to space the electrodes at a distance of 1.25 times their length to avoid overlapping resistance gradients so can take many rods to achieve even a less than 200 ohm earth in bad locations , the actual resistance required may be much less than that value.
 

Deepgreen

Established Member
Joined
12 Jun 2013
Messages
6,392
Location
Betchworth, Surrey
At Betchworth, one of four cabinets adjacent to the EB platform entrance path has such a cover. One of the other cabinets has this on it!
15699720356_ce92d2ed82_k.jpg
 

Robson689

Member
Joined
6 Jul 2014
Messages
11
I find it hard to believe that this equipment isn't earthed. No matter how old it is.
 

Laryk

Member
Joined
11 Jun 2011
Messages
188
Location
Taiwan
I find it hard to believe that this equipment isn't earthed. No matter how old it is.

Many assets associated with signalling has an IT Earth system. That is, the earth is connected to ground via a high ohm resistor. Technically it is earthed, but dangerous voltages can happily exist with minimal fault current.
 