Allowing for the existing timetable as the baseline is massively under-engineering?No I'm suggesting engineering for the requirements of the route not massively under-engineering which you are assuming to help self justify your thinking.
If they want additional trains, then that would put in in the project scoping phase.
Or allowances would be made for additional substation capacity to be cheaply added later should the demand arise if it is merely aspirational.
The topology I propose would allow a substation to be added cheaply at intermediate points should traffic demand increase, and could be any size you wish up to the maximum rating of the rail itself, depending of what drops out of your output specification.
So best not have any electrification at all?The entire SWML timetable is still limited by decisions taken planning during the Bournemouth electrification project 54-55 years ago so best not to repeat with similar under engineering in the future?
Because that is where this argument goes.
As the reports into problems with infrastructure projects like GWRM have stated, overly specified infrastructure is a massive problem for the railway and in British infrastructure projects more generally.
That would drop out of the detailed project specification phase. But given the low traffic density on routes that I am considering I can't see a 33kV feeder cable being a reasonable solution.In many locations the only need for DNO network enhancements would be rail electrification so the cheapest way to pay for it is doing it directly especially when you see the DUOS charges as well.
There is a maximum of four CLass 444 units west of Salisbury given the timetable and train length restrictions - that would imply a total maximum load around 8MW... which is getting on for the rating of a single 11kV feeder, let alone a 33kV one.
Many of the commenters started citing figures to justify their positions which are well away from the traffic densities on the routes I am considering for this topology.Given that everyone else with experience doesn't agree with your analysis might suggest some more detailed recalculation is needed?
They appear to be commenting based on third rail retaining the traditional Southern Region derived topology which takes no account for developments in controlled rectifier technology.
If they want me to run calculations for a given route, give me said project and I will try to run numbers for it.
In some cases indeed a HV fed substation would be the best solution - the key thing here is by breaking up the quanta of rectification and spreading it along the line, engineered so they can cooperate, we can drive losses down and ameliorate many of the cited problems with third rail as a solution
EDIT:
Also why does a Class 700 have so much installed power? (5000kW at rail?)
It is 12 cars long, but then the 100mph Class 707 which is five cars long and is also a Desiro city only has 1200kW installed power, both according to Siemens.
Even scaling that to ten cars only gives me ~2900kW
Is this just an AC versus DC thing?