Earth bonding on hand rails.

Status
Not open for further replies.

morgz94

New Member
Joined
1 Apr 2020
Messages
2
Location
Wantage
I live close to an unmanned unsignalled foot crossing over the Great Western MAin Line. I've noticed that there is some heavy guage bonding attached to the base of the safety railing either side of the crossing. I couldn't get a photo as I had left my phone behind. Could anyone tell me please what the purpose of this is? Thanks.
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

Tio Terry

Member
Joined
2 May 2014
Messages
1,178
Location
Spain
Safety. All metalwork is bonded together to avoid different potentials across two different earths within touching distance.
 

edwin_m

Veteran Member
Joined
21 Apr 2013
Messages
24,883
Location
Nottingham
We used to get a warning that if you cut through something like a metal conduit alongside an AC electrified route a dangerous voltage could appear between the two halves, so you should electrically connect them by attaching a wire before making the cut.

This is, I guess, because some of the traction return current flows through the earth around the conduit, by a mixture of leakage and induction, so there will be a voltage gradient through the earth. As the conduit is a better conductor than the earth, the two halves it will be at the same potential as the earth some distance away in each direction so the difference will be large.

Electrically connecting the handrail on each side of the crossing will avoid a similar hazard if someone could touch both at once. This is as well as the various other hazards mentioned above.
 

MarkyT

Established Member
Joined
20 May 2012
Messages
6,245
Location
Torbay
And because the hand rails are close to or within the fall zone of the live catenary, the bonds are rated to deal with a full fault current (IIRC 12kA) so your normal domestic equipotential earth wire isn't enough.
That fault current figure surprised me at first but when I considered the often vast size of 25kV substation areas and the large number trains within one that could be drawing current simultaneously it makes sense. While 750V currents are so much higher per train, the substation areas on DC are tiny by comparison.
 

satisnek

Member
Joined
5 Sep 2014
Messages
888
Location
Kidderminster/Mercia Marina
I can remember standing at one of the platform ends at Glasgow Central in the late 1980s, by a metal railing where one platform face finished before the other. This railing was slightly loose and wobbly, and touching it I could feel a fairly strong tingle. Things were rather more lax back then!

It's the same principle used, apocryphally, by farmers who had high tension power lines running across their land and obtained free electricity without making a physical connection!
 