London North Western wasn't accepting any tickets so if you live in St Albans for example, you were prevented by using the TOC to travel from London to St Albans via Watford Junction.

Not sure what kind of service they had but I'm sure they always accepted TL in the past?

When LM was a GoVia company, ticket acceptance was easy. Now that they are Abellio, it is done less often.

However I know for a fact that LNW did accept TL tickets, as I know several people who went that way no problem (and had tickets checked).
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

HSTEd

Veteran Member
Joined
14 Jul 2011
Messages
16,722
950MW of wind disappeared, as well as around 500MW of gas and solar each according to gridwatch. Thats 2 GW of loss in a few minutes. That's fairly substantial. It also happened at roughly peak demand, meaning there was a lot less spare capacity in the system as backup.
2GW of loss is somewhat worrying because a single large PWR like the ones at Hinkly Point C is ~1600MWe......
 

forty_two

Member
Joined
10 Feb 2010
Messages
6
Is anyone able to confirm if it was specifically the frequency swing that caused the 700 failure, or whether it was merely the fact that power was lost for a time?
 

Bald Rick

Veteran Member
Joined
28 Sep 2010
Messages
29,194
Is anyone able to confirm if it was specifically the frequency swing that caused the 700 failure, or whether it was merely the fact that power was lost for a time?

That’s not been confirmed, publicly or otherwise.
 

hwl

Established Member
Joined
5 Feb 2012
Messages
7,398
Is anyone able to confirm if it was specifically the frequency swing that caused the 700 failure, or whether it was merely the fact that power was lost for a time?
They have survived powercuts previously, there was something different about this one.
 

bramling

Veteran Member
Joined
5 Mar 2012
Messages
17,768
Location
Hertfordshire / Teesdale
Thanks for the info; I'm actually quite surprised it doesn't - so the LU could be affected by any "strikes" by power workers (as could trains)? He asks remembering the 70's!!

It seems the answer to that is yes. But remember the whole of LU can be stopped by a few of their own electrical control room operators not working for whatever reason! (Although LU have made some attempt at training some managers as emergency cover staff - which given the highly specialised nature of the role in question is a rather dubious move IMO).
 

agourdie

Member
Joined
8 Apr 2015
Messages
10
30 were stranded but some of those rebooted eventually so less than 30...

23/7 split
Was on a northbound train stuck in St Pancras station. Driver did a reboot which took 5 minutes. Train eventually departed south to Brighton
 

AM9

Veteran Member
Joined
13 May 2014
Messages
14,264
Location
St Albans
London North Western wasn't accepting any tickets so if you live in St Albans for example, you were prevented by using the TOC to travel from London to St Albans via Watford Junction.

Not sure what kind of service they had but I'm sure they always accepted TL in the past?
That certainly wasn't my experience. I alighted a westbound Circle line train at Farringdon at about 17:40. When I arrived on the northbound TL platform there was an 8-car 700 there, quite full with one pair of doors open but all others closed. After about 5 minutes, they were opened and it was emptied. There was a cluster of passengers surrounding a uniformed member of staff asking questions about how to get to various destinations. I managed to ask between two of them: "are they accepting TL tickets at Euston?" He said yes so I went back to the LU platforms and boarded the first westbound train to Euston Square. On checking RTT, I went to the P9,10 & 11 ramp as there was a Tring train due at 18:34. I asked a uniformed staff member whether they were accepting TL tickets and he said yes. He asked me of my destination to which I said St Albans Abbey via Watford Junction so he said that I should get an MKC bound train from P9, which was fast to WFJ so I would be in time for the 18:56 Abbey Flyer.
All went well and I was in SAA on time at 19:12. So there was no issue with ticket acceptance for me.
 
Last edited:

Aictos

Established Member
Joined
28 Apr 2009
Messages
10,403
That certainly wasn't my experience. I alighted a westbound Circle line train at Farringdon at about 17:40. When I arrived on the northbound TL platform there was an 8-car 700 there, quite full with one pair of doors open but all others closed. After about 5 minutes, they were opened and it was emptied. There was a cluster of passengers surrounding a uniformed member of staff asking questions about how to get to various destinations. I managed to ask between two of them: "are they accepting TL tickets at Euston?" He said yes so I went back to the LU platforms and boarded the first westbound train to Euston Square. On checking RTT, I went to the P9,10 & 11 ramp as there was a Tring train due at 18:34. I asked a uniformed staff member whether they were accepting TL tickets and he said yes. He asked me of my destination to which I said St Albans Abbey via Watford Junction so he said that I should get an MKC bound train from P9, which was fast to WFJ so I would be in time for the 18:56 Abbey Flyer.
All went well and I was in SAA on time at 19:12. So there was no issue with ticket acceptance for me.

Maybe but ticket acceptance should be both inbound and outbound at Euston, as it was they were only accepting outbound tickets.

Yes I know that’s the right move but for those who needed to get south of the river they needed inbound tickets to be accepted too.
 

Aictos

Established Member
Joined
28 Apr 2009
Messages
10,403
A good part of Central Europe, and even Germany, gets a fair proportion of its gas from Russia. Politics doesn’t really come into it. If the price is right...




When LM was a GoVia company, ticket acceptance was easy. Now that they are Abellio, it is done less often.

However I know for a fact that LNW did accept TL tickets, as I know several people who went that way no problem (and had tickets checked).

Indeed and change of TOCs should not mean changes to ticket acceptance in any case, LNR were partly to blame as they weren’t clear enough on twitter
 

yorkie

Forum Staff
Staff Member
Administrator
Joined
6 Jun 2005
Messages
67,800
Location
Yorkshire
Just a gentle reminder that this is about the rail disruption; any other topics are very welcome but they do need to be in a suitable thread in the correct area of the forum.

To discuss National Grid issues please use this thread: https://www.railforums.co.uk/threads/is-the-national-grid-sufficiently-resilient.188283/

If you see an off topic post, please do not reply to it in the thread. If you wish to reply, please post a new thread. Please report the first off topic post and let us know the details; we might be able to move posts into the correct thread. However this is time consuming and it is better if people create new threads themselves.
 
Last edited:

ashkeba

Established Member
Joined
13 May 2019
Messages
2,171
Did the service normalise from noon like GTR said or are trains and crews still out of position leading to cancellations?
 

Elecman

Established Member
Joined
31 Dec 2013
Messages
2,903
Location
Lancashire
The book "Electrifying the East Coast" has a longer explanation but they have to be careful about where the railway gets it 25kv from and they need to make sure its separate from the grid.

Its to stop the railway 25kv OHLE becoming part of the 100kv grid should a fault develop in the national grid.
The issue is DNOs do not like large and variable unbalanced 2 phase loads being taken off thier 132 KV networks , hence the NationalGrid preference for all new Traction Feeders being taken off the 400 KV Grid.

There is no possibility of the Railway Traction supply back feeding the Grid as the reverse flow protection would instantly open the NG breakers
 

Elecman

Established Member
Joined
31 Dec 2013
Messages
2,903
Location
Lancashire
https://www.bbc.co.uk/news/uk-49300025 says
Let's hope that all the railway ones are run up regularly, the fuel tanks are de-sludged on schedule and that they have enough capacity for 12 hours or so...

Yes they are, and tested by drop testing every 3 months, ie not just pressing the start button, but by physically turning off the incoming supply thus simulating a power cut.
 

High Dyke

Established Member
Joined
1 Jan 2013
Messages
4,281
Location
Yellabelly Country
https://www.bbc.co.uk/news/uk-49300025 says
Let's hope that all the railway ones are run up regularly, the fuel tanks are de-sludged on schedule and that they have enough capacity for 12 hours or so...
Oh, yes. I spent a steady few hours on Thursday evening, Rest Day working, on a quarterly power test of the signalling in an area where I work. Test went so well I hadn't actually realised the 'mains' power had been restored until the sparky came up to see me.
 

mm333

Member
Joined
28 Aug 2008
Messages
570
Location
53.8331°N 1.7734°W

hwl

Established Member
Joined
5 Feb 2012
Messages
7,398
18k delay minutes and starting at 2 million squid attributed to 700/717 sit downs...
 

Hadders

Veteran Member
Associate Staff
Senior Fares Advisor
Joined
27 Apr 2011
Messages
13,177
It actually was normal for Saturday all day. Lots of cancellations (just crew shortages were not the listed reason)

Shed load of cancellations on the GN side tonight. No idea if they’re related to last night’s shenanigans. I suspect not as this is quite normal at weekends for GTR, despite the largest driver recruitment campaign in railway history over the last 5 years.
 

ashkeba

Established Member
Joined
13 May 2019
Messages
2,171
It actually was normal for Saturday all day. Lots of cancellations (just crew shortages were not the listed reason)
2R71 ROYSTON KNGX 23:20 Cancelled
Service cancelled due to a. shortage of train crew.
2C68 KNGX CAMBDGE 23:28 Cancelled
Service cancelled due to a. shortage of train crew.
9S68 BRGHTN CAMBDGE STP 23:30 Cancelled 23:31 Cancelled
Service cancelled due to a. shortage of train crew.
[...]
1T74 KNGX CAMBDGE 23:42 Cancelled
Service cancelled due to a. shortage of train crew.
[...]
1C93 CAMBDGE KNGX 23:58 Cancelled
Service cancelled due to a. shortage of train crew.
 

tsr

Established Member
Joined
15 Nov 2011
Messages
7,400
Location
Between the parallel lines
Were any London Underground operations affected by this? I guess Overground was affected due to the power cut at Clapham Jct.

The Victoria Line was completely suspended for quite some time!

The Tube was very badly affected in places. At one point the situation on the Victoria Line was looking akin to what happened to Thameslink... just underground!

pretty simple.
30 minutes to (incorrectly) perform boot up sequence.
another 6 1/2 hours trying to diagnose what went wrong

That’s not at all what happened.

I suspect 313s rule on the Moorgate route this weekend.

It does concern me how the 700s will perform in the winter when ice causes chaos on the overhead. I hope they are not going to be sitting down for hours if we get cold mornings.

They’re good in the winter, except the saloon heating, which can be abysmally unreliable.

Planned evacuation. But in any event nothing was running, so even if it had been ‘self evacuated’, it would have been less of a problem than normal.

At least one uncontrolled evacuation occurred in the area. Can’t confirm if it was the train pictured, but I strongly suspect it was. At least two other trains had major disorder reported onboard.

Were the 387s OK? I'm on one now and I think it's short formed (4 not 8) and no WiFi and it's whistling a bit like a door hasn't shut tight but that might just be the forecast high winds arriving early.

The whistling is probably a dodgy rubber door seal or one of the emergency hopper windows not being locked shut properly.

London North Western wasn't accepting any tickets so if you live in St Albans for example, you were prevented by using the TOC to travel from London to St Albans via Watford Junction.

Not sure what kind of service they had but I'm sure they always accepted TL in the past?

When LM was a GoVia company, ticket acceptance was easy. Now that they are Abellio, it is done less often.

However I know for a fact that LNW did accept TL tickets, as I know several people who went that way no problem (and had tickets checked).

Yes, LNR were accepting TL tickets, though I seem to recall that this took a while to get on the website.

It is not done less often because it’s now an Abellio TOC. There is no real link there. GTR ask for LNR to accept their tickets regularly, and it’s virtually never refused. Only the long distance operators (LNER and VTWC) tend to occasionally refuse to accept GTR tickets, but that’s changing, since LNER have been through a bit of a bad patch and had to ask for a lot of help themselves.

Did the service normalise from noon like GTR said or are trains and crews still out of position leading to cancellations?

Thameslink service recovery was astonishingly good. Virtually the whole service startup was flawless after about 0500 on Saturday, with just a few Sutton/Wimbledon cancellations to start with.

The only major issue for much of the day was a 20mph speed restriction through Clayton Tunnel - even the major trespass issue at Wimbledon was cleared up quickly.

I am told that most of the controllers worked 16 hour shifts on Friday/Saturday night in order to pull it off... hats off to them (HM Government have sent thanks...)

Shed load of cancellations on the GN side tonight. No idea if they’re related to last night’s shenanigans. I suspect not as this is quite normal at weekends for GTR, despite the largest driver recruitment campaign in railway history over the last 5 years.

It’s largely down to inflexible driver contracts and rostering. Although some drivers had to book on later today after finishing later last night.
 

pint

Member
Joined
11 Aug 2019
Messages
22
First post on here, so please be gentle...

Powercuts, rare that they are ( at the moment) can happen, but why is the rail network so vulnerable???
if a train loses power then the staff/crew on board should be able to restart it, not some remote technician - what the hell is going on when what should be basic systems are so complex??
 

ExRes

Established Member
Joined
16 Dec 2012
Messages
5,830
Location
Back in Sussex
First post on here, so please be gentle...

Powercuts, rare that they are ( at the moment) can happen, but why is the rail network so vulnerable???
if a train loses power then the staff/crew on board should be able to restart it, not some remote technician - what the hell is going on when what should be basic systems are so complex??

Rather than everyone queuing up to blame the railway, perhaps those whizz kid, cannot do wrong, always perfect computer experts should have to explain why they left such an enormous hole in their system, in my experience any computer system is always more complicated than it needs to be in order to keep the power within the IT department
 

rogercov

Member
Joined
8 Feb 2019
Messages
185
Location
Coventry/London
First post on here, so please be gentle...

Powercuts, rare that they are ( at the moment) can happen, but why is the rail network so vulnerable???
if a train loses power then the staff/crew on board should be able to restart it, not some remote technician - what the hell is going on when what should be basic systems are so complex??
I'll try to be gentle!
As far as I can deduce, based on the discussion so far, it was not as simple as a train losing power.
This event was unusual in that the loss of generating capacity in the National Grid caused the mains frequency to drop to around 48.9Hz or below. This is well outside the allowed/agreed tolerance. This triggered some controlled power disconnections in some parts of the country but as far as I know, traction current on main lines was affected only briefly, if at all. There were some signalling problems but only temporary ones.
Most trains carried on running. DC lines were unaffected. Most trains on the ECML and MML would not have been affected by this power disturbance, other than getting stuck behind those that were affected.
Speculation so far is that the initial drop in mains frequency may have caused the computer on board the newer 700 and 717 units to interpret this as a far more serious fault, which was difficult for the driver to recover from with a normal reset procedure.
If this is the case, then the manufacturers will learn from it and update the software to tolerate this scenario. I'm guessing that it's not something they tested as they did not think it would happen.
A computer is only as good as the people who programmed it and those who specified the requirements!
If this is the reason, and it's still to be confirmed, there will be a battle between National Grid (who should not have allowed the mains frequency to drop so low) and Siemens (who should have programmed the trains to be more tolerant).
 

rogercov

Member
Joined
8 Feb 2019
Messages
185
Location
Coventry/London
I'd better correct this one before anyone accuses me of being unkind to Siemens.

If this is the reason, and it's still to be confirmed, there will be a battle between National Grid (who should not have allowed the mains frequency to drop so low) and Siemens (who should have programmed the trains to be more tolerant).

There was probably no requirement for them to make the trains more tolerant. No doubt they designed the software to a rigorous specification - no more, no less - so that if there were a change in requirements, they could make more money out of us.

However, I presume all AC traction is synchronised with the Grid (I'm sure someone will correct me if I'm wrong). If that's the case, it's interesting that the Bombardier 710s, despite all their earlier software problems, carried on running throughout this event.
 
Joined
5 May 2015
Messages
66
Location
Dunblane
I'd better correct this one before anyone accuses me of being unkind to Siemens.

If that's the case, it's interesting that the Bombardier 710s, despite all their earlier software problems, carried on running throughout this event.

It is also pertinent to remind ourselves that the inferior Siemens product was foisted upon us by the Department of Transport, at the expense of the Bombardier bid to build the rolling stock which was rejected.
 