OHLE over LU 4th rail

Status
Not open for further replies.

joeykins82

Member
Joined
24 Jul 2012
Messages
601
Location
London
I know the explanation of why 3rd rail DC and OH 25kV AC can't coexist for long sections (cheers to everyone who has patiently explained this one in the other threads about the Basingstoke-Southampton upgrade to AC) but I was thinking about the shared NR/LU sections, Harrow-Amersham in particular, and wondering whether it'd be possible for overhead AC to happily exist alongside 3rd & 4th rail DC? As I understand it the voltage return for LU is via the 4th rail so does this mean that the issues with the 2 systems being installed in parallel wouldn't apply, or am I demonstrating my naivety and coming up with an idea that would electrocute anyone travelling on an S stock service?

Explanations much appreciated!
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

steamybrian

Established Member
Joined
26 Nov 2010
Messages
1,744
Location
Kent
There are many places around London/South East where 3rd rail and OH 25kv AC co-exist over the same track. At stations-- Drayton Park, Farringdon, Ebbsfleet International and Ashford International are some examples. Sections of dual electrification exist on the West London Line north of Shepherds Bush and there may be some in the Stratford or Willesden area.
As far 4th rail and 25kv ac OH being together I am unsure but Drayton Park still has 4th rail in place but unsure if it is used. Someone may identify somewhere?
 
Last edited:

cle

Established Member
Joined
17 Nov 2010
Messages
4,008
I could only think maybe somewhere around Willesden Jn/Harlesden/Stonebridge but I can't actually think of any. Possibly around Barking or Upminster?

Should be no different to 3rd rail and OHLE - most examples are stationary, but they're going to have the whole section from Farringdon to City as both I believe.
 

joeykins82

Member
Joined
24 Jul 2012
Messages
601
Location
London
Oh I know overhead AC and 3rd rail DC is possible for small sections but as discussed elsewhere it's impractical for larger sections. I was wondering whether a larger section like Harrow to Amersham could be wired with overhead AC without affecting the 3rd & 4th rail DC traction, or whether Chiltern would have to use dual voltage stock for via Amersham services. Or, indeed, if it might lead to the end of shared operation on the lines with either Chiltern only operating via Princes Risborough (with requisite doubling of the line through to Aylesbury and onwards to MK/Bedford) and Metropolitan Line taking over services to Aylesbury, or NR taking over the fast lines from Harrow and all Metropolitan Line services going in to Watford Junction. I don't the last option would be particularly desirable since it'd limit any useful bonuses from the Croxley link such as direct Watford Junction to Aylesbury movements.
 
Last edited:

ole man

Member
Joined
6 Jul 2011
Messages
739
Location
LEC5
What is it on the NLL at Highbury & Islington 3rd or 4th rail?.
I know that all the OHLE Structures during the recent upgrade had to have insulated washers between the nuts and bolts.
This also applies to the signals on the Thameslink route, there's 1 that i know of at City Thameslink.
Its at the Farringdon end behind the railings mounted of the tunnel face.
 

jopsuk

Veteran Member
Joined
13 May 2008
Messages
12,771
the ELL is 3rd rail, and the NLL uese to have 3rd rail sections.

Having been following the explanations as to why short sections for changeover of DV are OK but long running sections are bad (including details of how the longish-Thameslink section works) I too am intrigued as to whether say the Watford DC could be turned into true 4th rail with seperate overhead power for the LO services.
 

ole man

Member
Joined
6 Jul 2011
Messages
739
Location
LEC5
The reason that they don't share the same routes for very long is that DC current is highly corrosive to metallic structures, hence why above i said that all new OHLE masts on the NLL have plastic insulated washers.
This also applies to signal gantry's has also stated above, lineside phones if base is metallic.
This problem has existed since the beginning of using DC current, and the only solution is to have insulation between any DC current and any metallic structure that is close by.
 
Last edited:

jopsuk

Veteran Member
Joined
13 May 2008
Messages
12,771
LU trains do not operate under OHLE on any part of the system.

Indeed, but the question is, with the caveat of needing suitable insulation as ole man says, whether the problem of the interaction between DC and AC the prevents Southampton-Basingstoke having both OLE and 3rd rail would be completely removed if it was OLE and 3rd/4th rail, where the rails form no part of the DC circuit whatsoever and the AC trains would in theory never come into contact with the DC circuit.
 

HSTEd

Veteran Member
Joined
14 Jul 2011
Messages
16,633
Would this not require major modifications to the trains however, requiring the current 750V bus to be split into a pair of smaller bus lines that are insulated against a potential difference of 1500V between them? (It would make sense to go for 750/-750V for the two rails).
 

DXMachina

Member
Joined
24 Oct 2011
Messages
652
A lot of places that appear to be 4-rail are actually 660v third rail with a centre conductor bonded to one running rail, added to allow LU stock to traverse a third-rail network

The difference is the voltages (+660/0 not -210/+420) and the earthing...
 

John55

Member
Joined
24 Jun 2011
Messages
800
Location
South East
Would this not require major modifications to the trains however, requiring the current 750V bus to be split into a pair of smaller bus lines that are insulated against a potential difference of 1500V between them? (It would make sense to go for 750/-750V for the two rails).

There is no need to go to -750V to +750V. The Mersey used +600V to 0V 3rd/4th rail for many years with the LMS (and MR) trains switching from 3rd to 4th rail operation at Birkenhead Park. I do not believe it was more than 2 contactors and an extra pick up shoe to be fitted plus a little care in designing the wiring.

I don't know how much current escapes from the two live rails on the LUL lines and if it finds a path to earth via the running rails. I suspect the effects on the LUL signalling would be the chief cause of concern.
 

HSTEd

Veteran Member
Joined
14 Jul 2011
Messages
16,633
There is no need to go to -750V to +750V. The Mersey used +600V to 0V 3rd/4th rail for many years with the LMS (and MR) trains switching from 3rd to 4th rail operation at Birkenhead Park. I do not believe it was more than 2 contactors and an extra pick up shoe to be fitted plus a little care in designing the wiring.

I don't know how much current escapes from the two live rails on the LUL lines and if it finds a path to earth via the running rails. I suspect the effects on the LUL signalling would be the chief cause of concern.

Tube type trains have separate pickup shoes for each bogie, this means they do not have to worry about how the current gets back to the negative rail.

Main line trains have a 750V bus (with some exceptions like the Class 313s), if you are going to return the current to the fourth rail rather than the running rails you will need a second bus line at the fourth rail voltage which must be able to handle the same currents as the normal one.

The only way to ensure that you do not add more mass to the train is to cut the current in each bus in half by doubling the voltage between the two rails compared to the normal one between the third rail and running rails.
 

es373

Member
Joined
19 May 2011
Messages
468
Location
London
If there is 3rd rail with OHLE on the same section of track, I wonder if OHLE could induce a voltage in to the third rail?
 

John55

Member
Joined
24 Jun 2011
Messages
800
Location
South East
Tube type trains have separate pickup shoes for each bogie, this means they do not have to worry about how the current gets back to the negative rail.

Main line trains have a 750V bus (with some exceptions like the Class 313s), if you are going to return the current to the fourth rail rather than the running rails you will need a second bus line at the fourth rail voltage which must be able to handle the same currents as the normal one.

The only way to ensure that you do not add more mass to the train is to cut the current in each bus in half by doubling the voltage between the two rails compared to the normal one between the third rail and running rails.

I assume you wrote this when very tired as it is nonsense. Trains may or may not have a power/return bus but all have a positive feed to the power equipment from the 3rd rail and a return back to the running rails or the 4th rail. In the case of a 4th rail return the cable carrying the return current goes to the appropriate shoe, in the case of a 3rd rail supply the cable goes to the axle of the wheelsets via a contact usually in the axlebox. There is no need for any change in voltage or change in current rating when switching between 3rd and 4th rail operation as demonstrated in my example of the changeover at Birkenhead Park between the LMS and the Mersey Railway.

One could design a system using +750V and -750V as the SER proposed in the 1920s but it has nothing to do with the difference between 3rd and 4th rail design.
 

es373

Member
Joined
19 May 2011
Messages
468
Location
London
Running a current through an axle box? Are you sure you are not tired as this would cause catastrophic damage to the axle bearing thus causing a derailment or seized wheelset.

I think the cable you are referring to is the axle box earth fault detection where if current is sensed going through the box then there should be a warning in the cab or the HSCB/VCB will open.
 

John55

Member
Joined
24 Jun 2011
Messages
800
Location
South East
Running a current through an axle box? Are you sure you are not tired as this would cause catastrophic damage to the axle bearing thus causing a derailment or seized wheelset.

I think the cable you are referring to is the axle box earth fault detection where if current is sensed going through the box then there should be a warning in the cab or the HSCB/VCB will open.

Not through the bearings but the last I heard the normal transfer of return current was via a wiper/brush on the end of the axle therefore mechanically in the axlebox. This will not of course apply to an inside frame bogie! There are lots of ways this could be done and may well be becoming obsolete.
 

hedpe

Member
Joined
3 Nov 2010
Messages
80
313's have an axle brush box for ground where the running rails are 0v. There is no direct physical contact between the train and the 4th rail that exists between moorgate and drayton park.
 

HSTEd

Veteran Member
Joined
14 Jul 2011
Messages
16,633
I assume you wrote this when very tired as it is nonsense. Trains may or may not have a power/return bus but all have a positive feed to the power equipment from the 3rd rail and a return back to the running rails or the 4th rail. In the case of a 4th rail return the cable carrying the return current goes to the appropriate shoe, in the case of a 3rd rail supply the cable goes to the axle of the wheelsets via a contact usually in the axlebox. There is no need for any change in voltage or change in current rating when switching between 3rd and 4th rail operation as demonstrated in my example of the changeover at Birkenhead Park between the LMS and the Mersey Railway.

And where will the fourth rail pickup shoes be?
If you don't want to allow current leakage to the running rails when that bogie does not have a pickup shoe in contact with the 4th rail, you will need some sort of bus along the train connected to the fourth rail pickup shoes. (Doing so would largely undermine the entire purpose of the fourth rail in the first place.)

As this bus carries the same current as the third rail pickup bus it must be of similar size.

Therefore the only way you can convert a train to fourth rail operation without requiring a net addition of bus lines to the train is to halve the current flowing through the traction package.

The only way to achieve this without reducing available power is to double the voltage between the 3rd rail and 4th rail compared to between the 3rd rail and running rail in a normal system.
This means +750V and -750V.

Converting a main line train to 4th rail is an engineering nightmare.
 

Dstock7080

Established Member
Joined
17 Feb 2010
Messages
2,741
Location
West London
LU trains now only have power bus lines within a motor car linking shoes/bogies and to just 1 adjacent trailer car for the supply to compressors/MA etc.
Power bus lines between motors cars no longer exist, except on the LTMuseums' '38 Stock.
 

John55

Member
Joined
24 Jun 2011
Messages
800
Location
South East
And where will the fourth rail pickup shoes be?


Usually under the front bogie.

[/QUOTE]
If you don't want to allow current leakage to the running rails when that bogie does not have a pickup shoe in contact with the 4th rail, you will need some sort of bus along the train connected to the fourth rail pickup shoes. (Doing so would largely undermine the entire purpose of the fourth rail in the first place.)[/QUOTE]


The return path to the centre (4th rail) pickup shoe is insulated from the vehicle chassis and wheels so if the shoe looses contact and there is no bus then the train looses power until the shoe regains contact. Exactly the same as for the 3rd rail shoe at pointwork or other gaps.

[/QUOTE]
As this bus carries the same current as the third rail pickup bus it must be of similar size.

Therefore the only way you can convert a train to fourth rail operation without requiring a net addition of bus lines to the train is to halve the current flowing through the traction package.[/QUOTE]

The current flowing in a circuit is the same at all points in the circuit. If a current of 1000A is required to drive a train from a 750V power source then 1000A flows from the 3rd rail shoe to the power equipment and 1000A flows back to the 3rd rail or the 4th rail. How the return current gets to the return path doesn’t affect the current demand or the voltage required. The only difference between 3rd and 4th rail operation is the termination of the return cable on the shoe or the axle/wheel and the isolation of the return side of the current path from the vehicle chassis..

[/QUOTE]The only way to achieve this without reducing available power is to double the voltage between the 3rd rail and 4th rail compared to between the 3rd rail and running rail in a normal system.
This means +750V and -750V.[/QUOTE]

The class 503s ran for 18 years (from 1938 to 1956) changing from 3rd rail operation on the former Wirral Railway (electrified on the 3rd rail) and then during the station stop at Birkenhead Park switched to 4th rail operation so they could operate on the Mersey Railway with no loss of performance. Both railways operated at nominal 600V.

[/QUOTE]Converting a main line train to 4th rail is an engineering nightmare.[/QUOTE]

The Mersey Railway managed to convert their trains in 1938 to operate off both 3rd and 4th rail systems with no difficulty. Seems odd if it is/was an “engineering nightmare”.
 

apk55

Member
Joined
7 Jul 2011
Messages
438
Location
Altrincham
The LU system is a nominally floating system with the power supply isolated from ground or only connected via resistors. I gather it is possible to short either conductor rail to ground or running rails without tripping the power supply (although a alarm would be tripped). A emergency shorting bar has to go between the two conductor rails.

Regulations for underground trains prohibited the use of train power bus bars, requiring each motor coach picking up its own supply normally from shoes at each end. This means that cars can be easily gapped when negotiating complex junctions although this is normal not a problem as there are several motor coaches in each train.

Where inter running with third rail trains is required there is a long section gap (with no conductor rails) at least a motor coach in length between the systems and the supply goes from floating to one side grounded as the centre conductor rail is hard connected via high current cables to the running rails.
For the lines into Moorgate which were converted from 4 rail to 3 rail operation the old centre conductor rail was left in place but also bonded to the running rails to improve the return current path. It is the return voltage drop that is the problem with combining a high voltage AC system with low voltage DC systems. Impose more than a few volts drop on the rails and a AC train transformer nearby will be driven into saturation, draw excessive current and trip out. I presume where dual electrified sections occur they make the return path very low resistance and use very frequent sub stations. Therefore I would not see any problem in dual electrification on LU 4 rail systems with high voltage AC (although the signalling system would need considerable work to immunise for both systems as at lest one of the running rails would be needed as a return current path).
 

Nym

Established Member
Joined
2 Mar 2007
Messages
9,098
Location
Somewhere, not in London
If there is 3rd rail with OHLE on the same section of track, I wonder if OHLE could induce a voltage in to the third rail?

Yes.

It would work much as the way as LU does at the moment (referred to in another post) with AC distribution feeding the DC network.

Although it would be dreadfully inefficent and anoying to be using a 1 phase supply, if we had two running lines it gets better as one could use a Scott T Transformer to feed the two running lines (Changes 2 phase to 3 phase), then taking current from both of these through a reverse set up to feed into standard 3 phase rectifiers for the DC circuits, or just use 1 phase rectifiers, but they're horrid!
 

es373

Member
Joined
19 May 2011
Messages
468
Location
London
Thought so.

Unless something could be brought up with earths and isolates either of the traction supplies as a train passes through the section.

Way too costly I would imagine, something for the RailWorks boys to have a play about with I think!
 

joeykins82

Member
Joined
24 Jul 2012
Messages
601
Location
London
... I would not see any problem in dual electrification on LU 4 rail systems with high voltage AC (although the signalling system would need considerable work to immunise for both systems as at lest one of the running rails would be needed as a return current path).

Thanks apk55, great explanation! I wonder if this might be considered as an option for the shared running sections at some point down the line? I guess it'll depend on just how "considerable" the signalling work would be.
 

Kneedown

Established Member
Joined
29 Dec 2007
Messages
1,768
Location
Nottinghamshire
The reason that they don't share the same routes for very long is that DC current is highly corrosive to metallic structures, hence why above i said that all new OHLE masts on the NLL have plastic insulated washers.
This also applies to signal gantry's has also stated above, lineside phones if base is metallic.
This problem has existed since the beginning of using DC current, and the only solution is to have insulation between any DC current and any metallic structure that is close by.

I'm having a bit of trouble getting my head around this one.
Anyone out there with a better knowledge of physics than i enlighten me as to how dc current causes corrosion to adjacent, unconnected structures, and ac doesn't?
 

Nym

Established Member
Joined
2 Mar 2007
Messages
9,098
Location
Somewhere, not in London
I'm having a bit of trouble getting my head around this one.
Anyone out there with a better knowledge of physics than i enlighten me as to how dc current causes corrosion to adjacent, unconnected structures, and ac doesn't?

From what I've read of the research done at Manchester (A Floor, UMIST Main Building) it's mainly to do with a constant current path causing a type of electrolosis as the electrons all flow in one direction, as does corrosion, as there is no net current flow in AC systems this doesn't happen.

There are papers on this but you need to be a subscriber to sci-verse to be able to read them, I get access through my IET membership so I'll have a quick check to see if there are any decent titles worth *cough* referencing in a subsiquent post for you.

EDIT:

Some free stuff found via Google Scholar...

This paper has some nice diagrams and explanation...
http://www.energy-cie.ro/archives/2010/n1-1-17.pdf

And this is another slant, but more general background.
http://www.jrtr.net/jrtr16/pdf/f48_technology.pdf

A bit more searching (that I might do myself later) could show up something, the IEEE has a lot on IEEExplore, but I've let my IEEE Membership lapse so I don't have access to that any more.
 
Last edited: