Hi all,
Just wondering if anyone would be able to explain how lamp proving works for flashing aspects in RRI and SSI regions?
Cheers
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

mr_towers

Member
Joined
22 Jan 2013
Messages
23
Location
Pitlochry
You might have some luck at the signalbox forums as well, they’re pretty good for hard(ish) core technical questions! Equally someone like AnnetsKey I’m sure will have something to contribute here.
 

Railsigns

Established Member
Joined
15 Feb 2010
Messages
2,504
Lamp proving relays are slow to release, so they're unaffected by momentary drops in current as well as momentary interruptions when a change of aspect occurs.
 

Annetts key

Established Member
Joined
13 Feb 2021
Messages
2,657
Location
West is best
The following applies to RRI areas:

The flashing yellow aspect of a conventional filament lamp is still supplied with a low current to keep the filament warn when its not “lit”.

Hence a special filament change-over relay is used in the head.

A flashing aspect unit has a separate output that feeds the flashing aspect lamp proving relay.

For SSI areas, everything is done by the SSI TFM signal module, including controlling the flashing and all lamp proving.
 

MarkyT

Established Member
Joined
20 May 2012
Messages
6,274
Location
Torbay
I recall that if the electronic flasher unit itself fails in a relay installation, it's designed to revert to providing a steady output, hence a steady single/double yellow, which is more restrictive than the flashing aspect intended, and thus a 'right side' failure.
 

Annetts key

Established Member
Joined
13 Feb 2021
Messages
2,657
Location
West is best
Yes, on failure of the flashing aspect system, the system drops out a proving relay. The junction signal then goes back to red and normal approach release applies. Hence the flashing single yellow signal will now become a steady single yellow. A flashing double yellow signal will now become a steady double yellow aspect.
 