Tyer’s type key token machines (the red one shown as Fig.2 on
www.railsigns.uk), they can be wired up in a number of configurations:
- Start/End/Intermediate Instrument that allows tokens to be withdrawn or returned.
- End of section Instrument, tokens can be returned but cannot be withdrawn.
If a line has token operated ground frames (GF), there can be a Intermediate Instrument at each GF, with the GF being unlocked by the token. There can be more than one GF each with it’s own Intermediate Instrument.
They can be configured as a requiring a signaller to give a release or be configured as a "No-Signalman Key Token" (NSKT).
Where the signaller is remote from all the token instruments, a token can be released only when permitted by the electrical interlocking, the signaller operating their control (button) and the requester operating the plunger on the token instrument they are at.
Special controls may be included. For example, the track circuit at the entrance may have to be proved operated (occupied) before a token can be released.
At the start of the section, the electrical interlocking may need to see that a token has been extracted before the protecting signal for the token section can be cleared.
At the end of the token section, the electrical interlocking may need to see that a token has been returned before the signal protecting the next section can be cleared.
Officially it’s the job of the S&T techinican to carry out token transfers. Unless special token carriers are provided, in which case where permitted, authority may be given to operations staff (such as a MOM) to carry out a token transfer. These special token carriers mechanically couple to the instrument so that you can only move tokens between the instrument and the carrier while it is attached. And when detached, you can’t get a token out of the carrier.