Hi,

can anyone help me with explaining exactly how the RC system works from start to finish? Doing a research project for degree on WCML and have come a bit stuck.

Essentially, I know the power is delivered from National Grid / DNO at 132kv, stepped down to 25kv and fed into the OHLE. Power is picked up by pantograph etc etc and anything left is passed back through the wheels to the Traction return rail.

Am I right in assuming the following: the return current is picked up by red Bonds and transferred to the return conductor (which usually hangs on the outside of masts). From this point on how does the power return to source etc?

Many thanks
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

Philip Phlopp

Established Member
Joined
31 May 2015
Messages
3,004

GRALISTAIR

Established Member
Joined
11 Apr 2012
Messages
9,034
Location
Dalton GA USA & Preston Lancs
I agree with Philip Phlopp - Garry Keenor’s work while not the absolute bible is extremely comprehensive, well illustrated and very readable. It is also free in electronic format.
 

Liamcronin

New Member
Joined
29 Oct 2020
Messages
4
Location
London
Thanks . I have looked at the OLE for railways book and while I. found it to be very informative, it didn’t provide me with the exact information I was looking for.

How do the red Bonds interact with the traction return circuit?
 

WAO

Member
Joined
10 Mar 2019
Messages
792
There's a thread under "infrastructure and stations" entitled,

"OLE - Classic Feeding - Return Conductor and Earth",

from way back in 2013/7 that has some informed discussion. You may have to Google the phrase to find it.

You probably need to understand the distinction between the three broad methods of overhead ac supply; Classic, Booster Transfomer (BT) and Auto-transformer (AT). The technology is still developing so expect some changes.

Are you doing a first degree or Masters'?

Good luck, anyway.

WAO
 

GRALISTAIR

Established Member
Joined
11 Apr 2012
Messages
9,034
Location
Dalton GA USA & Preston Lancs
And you can always look in the pinned thread at the top of the Infrastructure forum with a summary of most threads I could find about electrification.


This is thread I am referencing.
 
Last edited:

Liamcronin

New Member
Joined
29 Oct 2020
Messages
4
Location
London
Thanks again for the help,

Have looked through a lot of these forums/discussions, all very informative.
Would I be right in assuming the following;

The current is transferred, through the train wheels to the traction return rail.
From there, it is carried through red Bonds to the return conductor. Once in the return conductor, the booster transformers force the current back to the feed where it came in originally.?
 

AM9

Veteran Member
Joined
13 May 2014
Messages
14,898
Location
St Albans
Hi,

can anyone help me with explaining exactly how the RC system works from start to finish? Doing a research project for degree on WCML and have come a bit stuck.

Essentially, I know the power is delivered from National Grid / DNO at 132kv, stepped down to 25kv and fed into the OHLE. Power is picked up by pantograph etc etc and anything left is passed back through the wheels to the Traction return rail.

Am I right in assuming the following: the return current is picked up by red Bonds and transferred to the return conductor (which usually hangs on the outside of masts). From this point on how does the power return to source etc?

Many thanks
Please accept this as a constructive comment, but your words "Power is picked up by pantograph etc etc and anything left is passed back through the wheels to the Traction return rail" is not the best way to describe what happens. A better way would be to say: Current is collected (from the conductor wire by the pantograph and passed through the wheels to the traction current return rail. This hopefully doesn't sound just a pedantic reply but is intended to help.
 

GRALISTAIR

Established Member
Joined
11 Apr 2012
Messages
9,034
Location
Dalton GA USA & Preston Lancs
Please accept this as a constructive comment, but your words "Power is picked up by pantograph etc etc and anything left is passed back through the wheels to the Traction return rail" is not the best way to describe what happens. A better way would be to say: Current is collected (from the conductor wire by the pantograph and passed through the wheels to the traction current return rail. This hopefully doesn't sound just a pedantic reply but is intended to help.
Indeed and it is good practice to word things well if you come to write a MSc or PhD thesis or even a BSc/B.Eng project. Professors etc do like that and they will give a higher mark imho.
 

Liamcronin

New Member
Joined
29 Oct 2020
Messages
4
Location
London
Thanks again, and just to calm any worries, I am in the early stages and merely researching facts and procedures, and am a long way off anything remotely near a finished product, but all advi d / information welcome.

So am I right with what I assume about the return path for the current and how this interfaces with red Bonds?
 

Elecman

Established Member
Joined
31 Dec 2013
Messages
3,077
Location
Lancashire
Generally yes, crudely put the effect of the booster transformer where the passage of the traction current through the Primary winding ‘sucks’ the return current from the traction return rail through the Secondary winding into the return conductor
 

norbitonflyer

Established Member
Joined
24 Mar 2020
Messages
3,255
Location
SW London
Some confusion between power and current. It is the current which goes round the circuit. Power is generated at the power station and delivered to the train where it is used to drive the train (ultimately dispersed as heat, noise, and other forms of energy. As power is voltage x current, the amount of power in the running rails and the rest of the return circuit should be close to zero, as the rails are at Earth (zero) potential.
 

Richard Scott

Established Member
Associate Staff
International Transport
Railtours & Preservation
Joined
13 Dec 2018
Messages
3,970
Some confusion between power and current. It is the current which goes round the circuit. Power is generated at the power station and delivered to the train where it is used to drive the train (ultimately dispersed as heat, noise, and other forms of energy. As power is voltage x current, the amount of power in the running rails and the rest of the return circuit should be close to zero, as the rails are at Earth (zero) potential.
If we get really pedantic then power is energy changed from one form to another per second so really suppose we should say energy dissipated in the running rails and return circuit (as heat) should be close to zero? There will be some as there must be a voltage drop (drop in potential) for the return current to flow as the return circuit will have some resistance?
 

AM9

Veteran Member
Joined
13 May 2014
Messages
14,898
Location
St Albans
If we get really pedantic then power is energy changed from one form to another per second so really suppose we should say energy dissipated in the running rails and return circuit (as heat) should be close to zero? There will be some as there must be a voltage drop (drop in potential) for the return current to flow as the return circuit will have some resistance?
As will the OLE/3rd rail feed.
 

norbitonflyer

Established Member
Joined
24 Mar 2020
Messages
3,255
Location
SW London
If we get really pedantic then power is energy changed from one form to another per second so really suppose we should say energy dissipated in the running rails and return circuit (as heat) should be close to zero? There will be some as there must be a voltage drop (drop in potential) for the return current to flow as the return circuit will have some resistance?
The running rails should be at Earth potential, so the booster transformer would, I assume, provide a small negative potential on the return side of the circuit. Power losses in a conductor are I^2 x R where I is the current.
 

WAO

Member
Joined
10 Mar 2019
Messages
792
It might be worth while pointing out to the original enquirer that the Booster Transformer system is now out of favour, conversions being made to either Classic or AT. It would be questionable whether he should expend much effort studying such a system.

The earth point at the feeder station is at zero volts but the potential in the rail return must be progressively higher, (steel not being a very good conductor), perhaps a few tens of volts at the most. The BT was at attempt to reduce this. The maximum permitted touch voltage on the railway is I believe 60V.

WAO
 

Philip Phlopp

Established Member
Joined
31 May 2015
Messages
3,004
The maximum permitted touch voltage on the railway is I believe 60V.

EN 50122-1 refers and is calculated "as a function of time duration". AC values are 60V for >300s, increasing to a maximum of 865V for 0.02s, touch voltages are limited to 25V for engineering facilities to minimise risk of injury from reaction to higher touch voltages.

DC allows 120V >300s rising to 370V for 0.02s. This obviously doesn't apply to those Scalextric aficionados who can be found licking the third rail and erroneously claiming third rail is the superior traction system...
 

broadgage

Member
Joined
11 Aug 2012
Messages
1,094
Location
Somerset
As an aside, I would urge never treading on the running rails of an electric railway with bare feet. The relatively low voltage is unlikely to be dangerous in MOST circumstances, but could be dangerous in exceptional circumstances.
In general one should be well clear of the line in any case, but considering level crossings and the possibility of going unshod in holiday resorts.

The rails of street tramways likewise.
 

HSTEd

Veteran Member
Joined
14 Jul 2011
Messages
18,020
As an aside, I would urge never treading on the running rails of an electric railway with bare feet. The relatively low voltage is unlikely to be dangerous in MOST circumstances, but could be dangerous in exceptional circumstances.
In general one should be well clear of the line in any case, but considering level crossings and the possibility of going unshod in holiday resorts.

The rails of street tramways likewise.

Also even if the voltage is not directly dangerous, an uncontrollable muscle contraction might cause you to injure yourself in some other way.
Like reaching into the back of a CRT television and causing a discharge, which causes your arm to thrash around inside the set uncontrollably.
 