There are at least three types of neutral section.
The first and most common type is usually on low/medium speed lines where it's comp[act design makes siting easier. Pages 20 and 21 of the class 323 driver's manual show both the construction and operation of this type:
http://www.ttweb.co.uk/tra/323tm.pdf
The next type is the predecessor of that type where isolation was provided with vee-shaped bars on either side of the conductor centreline that carried the pantograph over a gap. these were placed in group of four that provided for a a short length of conductor to be grounded. The whole assembly was quite heavy and sensitive to physical instability if traversed at more than quite low speeds. I haven't seen any on running lines for some time but some remain on crossovers where speeds are low for track geometry reasons where they can be accommodated in the restricted length. I can't find any pictures of a complete installation but here is a drawing on a typical vee-shaped insulator:
http://www.indianrailways.gov.in/ra...ACTraction-II-P-I/imagesCh_3/Page_66_fig1.jpg
The third type is usually found on high speed lines. It is a derivative of the termination method of lengths of catenary/conductor wire where a terminating length is run in parallel with the next starting one. In this case there is a short section of OLE so there are two overlaps a few tens of metres apart. The short section can then be grounded when required. Their total length can be from less than 100m to over 400m.