Having seen many main line steam locos on 25KV electrified lines, I wonder why there are no flash-overs? Not from the safety valves as that's pure H2O, but from the exhaust. That comprises a lot of partially-combusted carbon particles, including heavy smoke particles, partially burned ashes, and small coals.

Why do flash-overs not occur?
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

starrymarkb

Established Member
Joined
4 Aug 2009
Messages
5,985
Location
Exeter
It has happened, a Kettle managed to short out Liverpool Street station.

[youtube]vQTinmPjS_o[/youtube]
 

CosherB

Established Member
Joined
23 Feb 2007
Messages
3,041
Location
Northwich
Thanks for that Starry. So it does happen, but is, apparently, no big deal?
 

ChrisCooper

Established Member
Joined
7 Sep 2005
Messages
1,787
Location
Loughborough
Of cource when the first 25kV electrification was taking place, steam was still pretty common. I think it was one reason for the use of 6.25kV in areas of limited clearance. Another concern was the fact that the soot might damage the overhead or the insulators, perhaps even causing shorts across the insulators. I don't think the problems were anything line what was predicted though.
 

scotsman

Established Member
Joined
6 Jul 2010
Messages
3,252
Flash-overs generally don't occur because exhaust gases are mainly composed of carbon, not in the form of graphite (which is conductive). As for the steam, well, water is a poor conductor and for it to cause a flash-over would mean that there was a very high saturation of water particles around the OLE
 

LexyBoy

Established Member
Fares Advisor
Joined
23 Jan 2009
Messages
4,478
Location
North of the rivers
Contrary to popular belief, 25 kV is not capable of jumping huge distances. The electric field strength at which the insulative properties of air breaks down is around 3 kV/mm, i.e. 25 kV won’t spark unless the air gap is ~8 mm or less (it’s slightly easier for moist air, but not drastically). Adding conductive particles to the air (e.g. water droplets) will reduce the dielectric breakdown threshold, but it needs to be reduced by ~100 fold in order to be able to spark over to ‘ground’ (the loco in this case), which would be very unusual – probably only possible in very confined situations such as in the video.

Not that I’d put my hands anywhere near OHLE of course :o
 

John Webb

Established Member
Joined
5 Jun 2010
Messages
3,097
Location
St Albans
Contrary to popular belief, 25 kV is not capable of jumping huge distances. The electric field strength at which the insulative properties of air breaks down is around 3 kV/mm, i.e. 25 kV won’t spark unless the air gap is ~8 mm or less (it’s slightly easier for moist air, but not drastically). Adding conductive particles to the air (e.g. water droplets) will reduce the dielectric breakdown threshold, but it needs to be reduced by ~100 fold in order to be able to spark over to ‘ground’ (the loco in this case), which would be very unusual – probably only possible in very confined situations such as in the video.

Not that I’d put my hands anywhere near OHLE of course :o
The air gap and electric field stength quoted above are measured using spherical electrodes probably at least a couple of cm in diameter. If electrodes are not spherical but pointed or otherwise irregular, the electric field strength in their vicinity can be much higher leading to breakdown of the air over a much larger gap - hence the possibility of flashover to parts of the human body from distances greater than the 8mm quoted above. So I'd definately keep my hands well away fron the OHLE!
 

matchmaker

Established Member
Joined
8 Mar 2009
Messages
1,516
Location
Central Scotland
Before steam was withdrawn, certain classes (Princess Coronations being one) were barred from travelling under 25kv OHL south of Crewe. These locos carried a diagonal yellow stripe on the cabsite.
 

LexyBoy

Established Member
Fares Advisor
Joined
23 Jan 2009
Messages
4,478
Location
North of the rivers
The air gap and electric field stength quoted above are measured using spherical electrodes probably at least a couple of cm in diameter. If electrodes are not spherical but pointed or otherwise irregular, the electric field strength in their vicinity can be much higher leading to breakdown of the air over a much larger gap - hence the possibility of flashover to parts of the human body from distances greater than the 8mm quoted above. So I'd definately keep my hands well away fron the OHLE!

This is also true - and is why lightning conductors have a spike at the top. Even so, there is a very large safety margin with the spacing of OHLE and anything conductive (rightly so!).
 