Why was the newcastle metro created as 1.5kv dc powered not 25kv ?

Status
Not open for further replies.

AHBD

Member
Joined
9 Sep 2022
Messages
143
Location
Northern Irelandm
I wondered why was the newcastle metro was created as 1.5kv dc powered not 25kv , when it was created from old heavy rail routes when 25kv ac had become standard?

Was it to allow regenerative braking? Cheaper installation / stock ?

How thick does a cable for at 1.5k have to b
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

HSTEd

Veteran Member
Joined
14 Jul 2011
Messages
18,644
The system was more or less bought off the shelf using German equipment, and the Germans weren't using 25kV at all at the time.

Lower voltage electrification is also cheap on low power demand lines like a comparatively low intensity metro.

If the original third rail equipment hadn't been run into the ground you may have ended up with something much closer to Merseyrail, it's contemporary.
 

snowball

Established Member
Joined
4 Mar 2013
Messages
8,111
Location
Leeds
On a system with frequent stops, DC saves carting transformers around.

Did they have in mind from the start the possibility of street running extensions?
 

swt_passenger

Veteran Member
Joined
7 Apr 2010
Messages
32,902
As said they bought fairly standard DC units, but when you get into the detailed description of the traction system they are actually using two 750V motors and associated control gear all connected in series. So they probably could have been ordered to work off a 750V supply relatively easily. But if using overhead collection that would result in a doubling of current, and larger contact wires etc.
 

AHBD

Member
Joined
9 Sep 2022
Messages
143
Location
Northern Irelandm
Thanks. Would it make any more sense for it to be 25kv in the future now that it will share 25kv lines using new dual voltage stock ie when 1.5kv wiring needs replaced?
 

hexagon789

Veteran Member
Joined
2 Sep 2016
Messages
17,011
Location
Glasgow
I wondered why was the newcastle metro was created as 1.5kv dc powered not 25kv , when it was created from old heavy rail routes when 25kv ac had become standard?

Was it to allow regenerative braking? Cheaper installation / stock ?

How thick does a cable for at 1.5k have to b
Energy costs.

Of the various proposals submitted by manufacturers - Permanent Series 750V motors powered from 1.5.kV overhead won the electricity consumption argument.

25kV was offered in the bids, but was deemed excessive for the requirements.

Thanks. Would it make any more sense for it to be 25kv in the future now that it will share 25kv lines using new dual voltage stock ie when 1.5kv wiring needs replaced?
I believe any further extensions will be 25kV, plus the shared section with Network Rail is to be converted, necessitating dual-voltage stock.

I don't believe the 555s have this capability surprisingly, unless I misses it?
 

ac6000cw

Established Member
Joined
10 May 2014
Messages
3,443
Location
Cambridge, UK
I believe any further extensions will be 25kV, plus the shared section with Network Rail is to be converted, necessitating dual-voltage stock.

I don't believe the 555s have this capability surprisingly, unless I misses it?
They don't have 25kV capability, but they do have provision for adding larger traction batteries (they have a small one for 'emergency' use as standard), so in appears the intention is that at least some extensions will be battery powered.

This is a quote from the Stadler data sheet:
The units are prepared for the integration of an energy storage system, allowing to serve potential extension lines added to the network in the near future.
 
Last edited:

AHBD

Member
Joined
9 Sep 2022
Messages
143
Location
Northern Irelandm
.....dual-voltage stock.

I don't believe the 555s have this capability surprisingly, unless I misses it?
It appears they dropped the 25kv voltage mode due to axle loading if all 3 proposed modes of 1kv5 , 25kv or battery where included which is interesting given the weight of batteries.. So I presume they will run on battery power under 25kv lines.

Modern railways metro
 

hexagon789

Veteran Member
Joined
2 Sep 2016
Messages
17,011
Location
Glasgow
They don't have 25kV capability, but they do have provision for adding larger traction batteries (they have a small one for 'emergency' use as standard), so in appears the intention is that at least some extensions will be battery powered.

This is a quote from the Stadler data sheet:
I noticed the mention of brake recuperation to storage batteries, but not how useful the stored energy would be (ie just shunting or whether off-wire running was feasible).

It appears they dropped the 25kv voltage mode due to axle loading if all 3 proposed modes of 1kv5 , 25kv or battery where included which is interesting given the weight of batteries.. So I presume they will run on battery power under 25kv lines.

Modern railways metro
I did wonder, given dual voltage capability was previously mentioned in the new stock procurement
 

DustyBin

Established Member
Joined
20 Sep 2020
Messages
3,850
Location
First Class
I once read (possibly on this forum!) that the tunnels would have had to have been built to a larger diameter to accommodate 25kv. I think it was to do with proximity of the cables to the surrounding infrastructure. This may not be true, it's just what I remember reading!
 

HSTEd

Veteran Member
Joined
14 Jul 2011
Messages
18,644
I would be incredibly surprised if 25kV ever reaches Sunderland.

I'd argue dual voltage NR units are far more likely if electric mainline trains ever do go to Sunderland
 

SeanG

Established Member
Joined
4 May 2013
Messages
1,300
I would be incredibly surprised if 25kV ever reaches Sunderland.

I'd argue dual voltage NR units are far more likely if electric mainline trains ever do go to Sunderland
Or heavy rail units using battery from Pelaw - Sunderland
 

edwin_m

Veteran Member
Joined
21 Apr 2013
Messages
26,705
Location
Nottingham
It was certainly pointed out when it first opened, that the Metro overhead wires were run under many existing bridges. Electrical clearance may play a part, but it's at least partly down to the lower roofline of the Metrocars compared with standard trains. The original Metrocars don't have regenerative braking so that couldn't have been a reason. I suggest the main one was avoiding having to put a transformer on each train.
 

Tetchytyke

Veteran Member
Joined
12 Sep 2013
Messages
14,872
Location
Isle of Man
The Metro was never meant to be a heavy rail system. It was much more akin to a tram system, to the extent that Metro-Cammell actually marketed the Metrocars as "supertram". And you don't get trams with 25kV overhead wires.

It'll only ever be an issue if Sunderland-Pelaw requires electrification for heavy rail, which I wouldn't see happening at least for another generation, if ever.
 

Vespa

Established Member
Joined
20 Dec 2019
Messages
1,733
Location
Merseyside
The Metro was never meant to be a heavy rail system. It was much more akin to a tram system, to the extent that Metro-Cammell actually marketed the Metrocars as "supertram". And you don't get trams with 25kV overhead wires.

You do now with Sheffield TOPS numbered dual voltage tram to Rotherham on NR tracks.
 

miklcct

On Moderation
Joined
2 May 2021
Messages
4,954
Location
Cricklewood
1.5kV DC is more suitable for a tunnelled metro operation because it's cheaper to build tunnels for 1.5kV DC operation due to the clearance requirement.
 

D365

Veteran Member
Joined
29 Jun 2012
Messages
12,162
You do now with Sheffield TOPS numbered dual voltage tram to Rotherham on NR tracks.
25kV capable - the Rotherham electrification is currently operated at 750Vdc.
 

43096

On Moderation
Joined
23 Nov 2015
Messages
16,772
25kV capable - the Rotherham electrification is currently operated at 750Vdc.
In which case I’ll throw in the new Cardiff Valleys sets, which are tram-trains with 25kV capability.
 

DanNCL

Established Member
Joined
17 Jul 2017
Messages
5,018
Location
County Durham
You do now with Sheffield TOPS numbered dual voltage tram to Rotherham on NR tracks.
25kV capable - the Rotherham electrification is currently operated at 750Vdc.
In which case I’ll throw in the new Cardiff Valleys sets, which are tram-trains with 25kV capability.
The Sheffield tram-trains have 25kV capability, but the wires to Rotherham are 750v DC like the rest of Supertram so the 25kV capability of the tram-trains is unused.

The South Wales tram-trains will be powered by 25kV and won't have any DC capability. All running away from 25kV will be done with batteries.
 

DustyBin

Established Member
Joined
20 Sep 2020
Messages
3,850
Location
First Class
The Metro was never meant to be a heavy rail system. It was much more akin to a tram system, to the extent that Metro-Cammell actually marketed the Metrocars as "supertram". And you don't get trams with 25kV overhead wires.

It'll only ever be an issue if Sunderland-Pelaw requires electrification for heavy rail, which I wouldn't see happening at least for another generation, if ever.

The current fleet is based an a German tram design (below solebar at least) but the system itself has very little in common with a tramway. It's more of a suburban rail network, similar to U-Bahn or possibly S-Bahn (there's considerable disagreement over which!).
 

Tetchytyke

Veteran Member
Joined
12 Sep 2013
Messages
14,872
Location
Isle of Man
the system itself has very little in common with a tramway. It's more of a suburban rail network, similar to U-Bahn or possibly S-Bahn (there's considerable disagreement over which!)

It's a weird mishmash, really. It's certainly not an S-Bahn- Merseyrail is the best UK example of that. The trains are lightweight and the stations are very basic, there's really very little difference between Metrolink's off-street sections and Metro. Even the underground sections are closer in feel to the Brussels pre-Metro than a U-bahn or even Merseyrail.

The new trains, which are a bit more heavy duty, will definitely move it more towards a U-bahn though.
 

DustyBin

Established Member
Joined
20 Sep 2020
Messages
3,850
Location
First Class
It's a weird mishmash, really. It's certainly not an S-Bahn- Merseyrail is the best UK example of that. The trains are lightweight and the stations are very basic, there's really very little difference between Metrolink's off-street sections and Metro. Even the underground sections are closer in feel to the Brussels pre-Metro than a U-bahn or even Merseyrail.

The new trains, which are a bit more heavy duty, will definitely move it more towards a U-bahn though.

I agree, it’s definitely a mishmash and doesn’t fit neatly into a category. That’s a good point re the new trains though, they’re decidedly U-Bahnesque.
 

SeanG

Established Member
Joined
4 May 2013
Messages
1,300
I agree, it’s definitely a mishmash and doesn’t fit neatly into a category. That’s a good point re the new trains though, they’re decidedly U-Bahnesque.
And indeed virtually the same as those used on the Berlin U-Bahn
 

Recessio

Member
Joined
4 Aug 2019
Messages
1,008
Location
London
Only in Britain could we end up with electric trains running on batteries on electrified tracks, christ almighty...
 

D365

Veteran Member
Joined
29 Jun 2012
Messages
12,162
And indeed virtually the same as those used on the Berlin U-Bahn
The new T&W trains are siblings of the Class 777, are they not? (descended from Berlin as you say)
 

hacman

Member
Joined
22 Jul 2011
Messages
444
The new T&W trains are siblings of the Class 777, are they not? (descended from Berlin as you say)
They're quite different from the Berlin units (Berlin have non-articulated cars for a start).

They're siblings in as much as they use similar technologies and components, but then again that would be the case for most of the products that Stadler offer across multiple categories.

https://www.stadlerrail.com/media/pdf/tbvg0713e.pdf - BVG units
https://www.stadlerrail.com/media/pdf/mmer0420e.pdf - Merseyrail 777s
https://www.stadlerrail.com/media/pdf/mmer0420e.pdf - Nexus 555s

Only in Britain could we end up with electric trains running on batteries on electrified tracks, christ almighty...

I think we're a long way off from that being the case here on Tyneside. And if it were to become a prospect, we could just as easily order a sub-fleet with 25kv capability, or even add a power-pack module into the existing consists as Stadler have done for other customers.
 

Haywain

Veteran Member
Joined
3 Feb 2013
Messages
20,078
Only in Britain could we end up with electric trains running on batteries on electrified tracks, christ almighty...
We don't actually have that. Instead we have electric trains running on diesel on fully compatible electrified tracks ...
 

61653 HTAFC

Veteran Member
Joined
18 Dec 2012
Messages
18,560
Location
Yorkshire
Only in Britain could we end up with electric trains running on batteries on electrified tracks, christ almighty...
I've long held the position that our insistence on putting all our eggs in the battery basket will come back to bite us on the rear end. I've yet to hear anything to avail me of this.
 