It is often the voltage drop between substations that limits the power available to trains. In addition the return voltage drop must be limited to a few volts for both safety and corrosion issues. The voltage drop represents a power loss or inefficiency and it also becomes difficult to detect faults. There are 3 possible ways of increasing the power availableMy understanding is that substations are supplied by lineside HV cables (33kV?) in separate troughing fed from a limited number of grid stations so no local issues and additional ones can go anywhere, halfway between is best for lower losses. There are/were restrictions on some lines due to heating of the rectifiers, more/longer peak trains and a basic off-peak service.
1/ Increase the voltage to the maximum possible, already done in most cases unless they can get regulations changed and new trains that can handle higher voltage.
2/ Reduce the resistance of the conductors. This would mean even heavier conductor rail (or a parallel feeder with links) and a massive return feeder with links to the running rails.
3/ Reduce the substation distance. A typical substation is a sizable building at least the size of a large double garage. Finding land in the right area could be a problem and getting access to it another, as it would ideally located midway between two existing substations. This would effectively double the number of substations on a section of track. And they are not cheap, excluding land and access provision they probably cost several million pounds.