Elecman
Established Member
There are no 11kv DNO feeders that I am aware of the smallest I've seen is 33kv
Chris Gibb's report [Page 64/163] mentions that an 11kV supply was used for the East Grinstead electrification project in 1987.There are no 11kv DNO feeders that I am aware of the smallest I've seen is 33kv
Probably steered deliberately by some clever "Sir Humphrey" in the Treasury or Department for Roads who probably had a very good idea of the eventual fallout in the hated rail industry ...
Source? With the feeder stations at the same spacing the I2R losses would be about nine times higher, and the discrepancy increases if the 25kV is autotransformer fed. For the same reason regenerative braking becomes more efficient too.Electrification. At 6KV DC the losses are equal to 25Kv AC. So,
Quite simply because the higher the voltage the lower the I2R losses. The longer the distance and the less intensive the service the higher the most economic voltage, even if that results in each train having to carry a transformer. Hence why trams have 750V, the few electrified heavy haul railways tend to go for 50kV, but practically every mixed traffic railway that has electrified post-war and hasn't been constrained by an existing system (and some that have been) has gone for 25kV. Power electronics has made some things possible, including potentially balancingg phase loads on the Grid at 25kV feeders, but it hasn't changed the laws of physics."25 Kv needs Expensive 400Kv substations Grid-fed Single-Phase. DC does not,
and can be fed from 11Kv or 33Kv local feeders. .......Why not cut out the 25Kv, and feed direct?
I have seen it suggested that the power supply on the northern reaches of the ECML is about at its limits and will need to be beefed up if extra electric trains are to be run.The ECML seems to be fed from 132kV lines (into 25kV AC), at least over the ECM5 section (York to Newcastle).
Source? With the feeder stations at the same spacing the I2R losses would be about nine times higher, and the discrepancy increases if the 25kV is autotransformer fed. For the same reason regenerative braking becomes more efficient too.
Quite simply because the higher the voltage the lower the I2R losses. The longer the distance and the less intensive the service the higher the most economic voltage, even if that results in each train having to carry a transformer. Hence why trams have 750V, the few electrified heavy haul railways tend to go for 50kV, but practically every mixed traffic railway that has electrified post-war and hasn't been constrained by an existing system (and some that have been) has gone for 25kV. Power electronics has made some things possible, including potentially balancingg phase loads on the Grid at 25kV feeders, but it hasn't changed the laws of physics.
The 400kV feeder stations are much further apart, for example there is one near Newton le Willows and the next one east will be beyond Stalybridge (not connected directly to OLE due to electrification delays, but designed to be in future). I imagine it would be possible to feed 25kV from local feeders too - the power demand per length of line would be similar, lower actually because 25kV is more efficient - but it isn't done because one big feeder is more economic than many small ones.
The skin effect is pretty much a non-factor at 50Hz.AC has something called IMPEDENCE, which DC does not. In practical terms, this means conductors of AC are not fully utilized (skin effect).
It's high enough that it significantly reduces current requirements, but low enough that insulation and clearance requirements are reasonable.Whats so magic about 25Kv?
But you need a lot more of them.400Kv Feeder Stations may be far apart, but, they are VERY large and expensive. Compared to 33Kv Substations. The Higher the voltage the more expensive the equipment, and the more space it
takes-up.
Considered and rejected, so Russia decided 25kV was better despite already having DC electrification at a lower voltage which would have made a DC conversion easier.6Kv DC Re-electrification was seriously considered in Russia in recent times.......And, even went right to government decision-making, where the proposal was rejected. This is where I got the
quote of parity with 25Kv AC.
That's why AC wires are the thickness they are, and most of the return current passes through return conductors rather than rails. If you needed less impedance you would use several wires rather than a fatter one.AC has something called IMPEDENCE, which DC does not. In practical terms, this means conductors of AC are not fully utilized (skin effect). This especially applies to steel rails, but manifests in all conductors to some extent. DC only has to deal with RESISTANCE.
I think the problems with AC in the UK are to do with delivery and standards rather than the system itself - BR managed to do it at competitive prices in the past. Who knows how much a new DC scheme would cost on NR if done today? The tram-train is not a good omen!Yes, I can see the point of 25Kv for High-Speed lines like HS2, but for most local
rail routes in UK, it is turning out to be horrendously expensive, and progress painfully slow, with 60% of the system still un-electrified, and Ministers claiming Diesel is good enough, here in the 21st
century.
As I've already suggested, pretty much every mixed traffic railway making the decision in modern times has settled on 25kV (little K big V by the way) - even some that had previously adopted a lower voltage.Yes, you COULD electrify at 60Kv AC, but would it be sensible?.....You COULD build railways to 7ft gauge too? but, didn t someone try that? Whats so magic about 25Kv?